Calling all AC techs. Why would a furnace run fine without the access panel?
When set for a call for heating, the Bryant furnacte, 376 CAV, will short cycle.
The ignition sequence is okay: combustion blower energizes, pressure switch closes, HSI energizes, gas valve opens, gas ignites, blower comes on. It runs for two minutes, then all but the blower stops. I get 33 fault code.
The blower motor - ok.
Capactior - ok
limit switches - all ok
Air flow - Return and Supply air are ok.
Dampers - not any
wiring and conections - ok
blower motor - rotation ok
combustion blower - ok (would be a different fault code
PCB - ok, is getting power.
When I tape down the door switch and leave the access panels off, the system will operate fine, until a call for heating stops.
So, the airflow is higher without the panels and it runs ok.
I can't think of any other reason, can you ?
Here is some additional information:
Unit is from 1994 but in excellent condition. Clean.
I changed blower speeds from Med low (standard setting) to Med Hi. no luck.
Did not check for a dirty evaporator but these people change the filter every month, probably.
The combustion vent is ok, double wall type B. It does have a long run of about 50 feet.
Motor was changed about 4 months ago.
I cleaned the centrifugal blades about 2 months ago.
Update:
Jumped Hi-Limit and system ran normally.
Blower amps .5
Gas Valve Pressure: 2.25 w.c. (3.5 is factory)
Blower wheel ok, not loose.
Ran system without filter, still got code 33.
Scoped Evaporator. Clean enough.
Taped up Supply plenum leaks.
Factory heat rise is 35-65.
heat rise with electric panel on was 59 ( 73 supply, 132 return); without panel was 53 (75 and 128).
System is 115,000 btu, 80 percent effeciency.
cfm with panel was 1450 cfm; cfm without panel was 1650.
More Information:
According to the Specification sheet for a 376CAV 060115
The gas pressure minimum is 4.5 w.c. - max is 14.5 w.c.
Airflow in Heating 1735 cfm.
376 CAV