Yahoo Answers is shutting down on May 4th, 2021 (Eastern Time) and the Yahoo Answers website is now in read-only mode. There will be no changes to other Yahoo properties or services, or your Yahoo account. You can find more information about the Yahoo Answers shutdown and how to download your data on this help page.

Vaillant combi-boiler and no CH?

I've had a new Valliant boiler (Pro 24) installed under a year ago and I am already experiencing issues with the Central Heating aspect of it.

I can give you the following information about it (I have had the original installer look at it but without repair so far). Does anyone else have any ideas about what may have gone wrong?

- Water pressure at cool is over 3.0psi

- Hot water running without problem

- Radiators have been bled fully with no air

- Magnaclean was installed to remove iron filing build-up from previous occupants lack of servicing, emptied in service just 4 days ago

- Firing under "SFH" mode forces water temperature to raise to maximum before cutting out, then sporadic lighting

- Pipes are clear as we have occasional heating (lasts no more than 15-30mins a time and then goes ice cold and struggle to reintroduce hot water into system)

- Manual dials on both HW and CH are at maximum

- Installed, but told that it has been disconnected, wireless thermostat

- No error messages

If anyone has any other ideas, I would be most appreciative.

8 Answers

Relevance
  • Anonymous
    1 decade ago
    Favorite Answer

    Hi, as John has said, LINKS 3&4 need to be linked, either via a room stat or a piece of wire.

  • 1 decade ago

    Since you are getting hot water I would first of all rule faulty ntc's (boiler stats). What you are describing sounds like a faulty diverter valve, possibly stuck in hot water mode. Or it may be an electrical fault, such as a bad connection to the diverter valve for example or even the pcb. Try looking at this first. If this is not the fault then as the boiler is under warranty, since you say it is less than a year old,then get Vaillant to look at it.

    Having said all this, you say there is no error code which is strange and suggests that there may not be any fault at all with the boiler and that there is no call for central heating. If the wireless stat is not connected, then check the terminal block where the mains cable is connected to the boiler. You should have live neutral and earth. Next to this you should see connections 3 & 4 which should have a link wire connecting them together. If there is no link wire install one. If there is a link wire check for lose connections.

    On another note you say the pressure in the system is 3psi. Do you really mean 3 BAR. If so this is much to high and should be reduced to between 1 and 11/2 bar when cold.

    Source(s): Domestic gas heating engineer
  • Anonymous
    5 years ago

    Vaillant Boiler Not Working

  • Anonymous
    1 decade ago

    Try turning the CH dial down. The influx of heat when it kicks in may trip any thermostats into shutting down because the temperature is too high.

    Vaillants are good boilers, so if there is no error message then it's most likely a component fault like pumps or motorised valves.

  • ?
    Lv 6
    1 decade ago

    The cold pressure is too high. Reduce it to 1.5 bar by either opening the safety valve or a bleed valve on a rad. If it is still under guarantee and the installer can't sort in straightaway ask Vaillant UK if they can send one of their own engineers. These big firms are usually very helpful when it comes to boilers under guarantee.

  • Anonymous
    5 years ago

    I've got the same boiler, (5 yrs old) but the opposite problem, water is leaking slowly out of the system and every few weeks we have to let more water in. Assuming you haven't had it serviced in a while, I think that's what you'd better do. Vaillant are quite good, they charge about £100, but you can check with them before you book the appt. I think you're right about it not being a good thing.

  • Anonymous
    1 decade ago

    As there is no prob with HW. First test the CH system -motorised valves and pump(s).

    If no luck then look at boiler.

  • 1 decade ago

    If your boiler is under 1 year old it should still be under warranty. Contact the person who installed it or call Vaillant.