Yahoo Answers is shutting down on May 4th, 2021 (Eastern Time) and the Yahoo Answers website is now in read-only mode. There will be no changes to other Yahoo properties or services, or your Yahoo account. You can find more information about the Yahoo Answers shutdown and how to download your data on this help page.
Trending News
Calculus for puzzlers, plug and chug for EEs?
A 24VAC circuit consists of 2 AWG#12 conductors
(Resistance ≈ 5.2 Ohms/km). The conductors supply
twenty eight .5 Ampere loads spaced equally at 2m for total
length 56m. The first two meters carry 14 Amperes.
the last two meters carry .5 Amperes.
What is the Voltage drop at the last device?
2 Answers
- EckoLv 77 years agoFavorite Answer
There are 2 legs, so just analyzing 1 at first.
The idea is to determine the average current (conceptual) through the 28 resistors.
This is not avoiding calculus, rather simplifying it. Because all the loads are equal the average is 1/2 the total.
Try it with 4 loads of 1A to understand. Make each section 1 ohm too. Draw it out, write the currents near each resistor...
The average current is the sum of all the load currents divided by the number of loads.
That would be (4A + 3A + 2A + 1A ) / 4 loads = 2.5A
Easy with only 4 loads, but with 28 loads tedious, so the average current is:
Iavg = 0.5 * ( (Number of loads * current per load) + ( 1 * current per load) ) = 2.5A
Next, 4 loads has 4 resistor sections, so 4 ohms (one leg).
Vdrop = I * R = 2.5A * 4 ohms = 10V.
Total is double that for 2 legs.
In your example:
With 28 loads of 0.5A
The average current for all the resistors is:
Iavg = 0.5 * ( (28 * 0.5) + 0.5) = 7.25A
The total resistance of one leg is 28 * 0.0104 = 0.2912 ohms
The voltage drop in one leg:
V = IR = 7.25A * 0.2912 ohms = 2.1112V
Double it for both legs = 4.2224V =====> answer
The voltage across the final load is 24V - 4.2224 = 19.7776V
- khalilLv 77 years ago
resistance of first connection is .....
4 x 5.2 = 20.8 milli-ohm and voltage drop = 20.8 x 0.5 = 10.4 milli-volt
if you add the second load ...voltage drop = 2 x 10.4 = 20.8 mV
and on 14th load >>> 14 x 10.4 = 145.6 mV