Yahoo Answers is shutting down on May 4th, 2021 (Eastern Time) and the Yahoo Answers website is now in read-only mode. There will be no changes to other Yahoo properties or services, or your Yahoo account. You can find more information about the Yahoo Answers shutdown and how to download your data on this help page.

? asked in Home & GardenDo It Yourself (DIY) · 3 years ago

When adding an additional outlet off an existing one with Wiremold, does the new outlet box need to be grounded if the starter box is?

I am chaining a new outlet off an existing one, if I ground the starter box, do I need to ground the new outlet box? Won t the new box be grounded from the starter box with the metal raceway? Any help is appreciated. Thanks

9 Answers

Relevance
  • ?
    Lv 7
    3 years ago

    Run a piece of bare conductor from the existing box, through the wiremold, to the new receptacle.

  • Anonymous
    3 years ago

    Definitely yes.

  • ?
    Lv 7
    3 years ago

    Run a ground wire from the existing outlet to the new one. Then the box will be grounded through the chassis of the outlet itself.

  • 3 years ago

    If you are using metal wiremold the raceway satisfies the Equipment Ground Conductor (commonly called a ground wire) requirement, but the receptacle needs to be grounded to the box at the next box.

    And if you do pull an EGC into the raceway then you need to connect it to the receptacle and the box. You would think the raceway should ground the box, it does seem the gradient or inductive difference in the ground would be negligible, but I don't pretend to know more than the code making panel that governs the requirement, and the NEC 250.148 requires all grounds be connected together and to the metal enclosure at every box that contains a termination.

    There are a couple of other scenarios that develop that make little sense, like I once pulled an additional 30A circuit into a 3/4" emt raceway that only had 20A circuits in it. The conduit satisfies the ground requirement, but in my haste I failed to notice that there was an existing (optional) #12 ground wire in the raceway, the electrical inspector wrote a correction notice, I pulled the ground wire out and then it passed.

  • 3 years ago

    do NOT trust the metal raceway as a ground. Current electrical code says you should wire in the ground [bare] to the outlet and the box

    Source(s): grampa
  • ?
    Lv 7
    3 years ago

    I'm assuming the wiremold you are referring to is some sort of conduit in this situation. Conduit is no longer considered to the ground alone, hasn't for some time. You are still suppose to run a separate ground, or at least in my state it was required, going on 20 plus years now.

  • 3 years ago

    The actual box DOES NOT need to be grounded, but the OUTLET should always be grounded. If this is even REMOTELY news to you, YOU shouldn't be installing outlets.

  • Jeff D
    Lv 7
    3 years ago

    It depends if the type of raceway is listed for grounding (I believe Wiremold is, but check it; plus the raceway has to be properly connected to the ground). Personally, I'd run a ground wire anyway just to be safe.

  • 3 years ago

    Anytime you terminate the Black, White or Red, terminate the ground.