Yahoo Answers is shutting down on May 4th, 2021 (Eastern Time) and the Yahoo Answers website is now in read-only mode. There will be no changes to other Yahoo properties or services, or your Yahoo account. You can find more information about the Yahoo Answers shutdown and how to download your data on this help page.

? asked in Science & MathematicsEngineering · 1 year ago

How to Calculate the size of Circuit Breaker for a Three phase load ?

Lets take a load that needs a power rating of 10kW and on voltage of 415V. (Vline) 240V Vphase

What size circuit breaker is needed for three-phase system?

P = 3 x VPH x IPH x CosФ

P = √3 x VL x IL x CosФ

If I use phase values do I need to divied the power by 3 (1000/3) before using the formula ?

Does it matter how the three phase system is connected Star or Delta ?

My calculation was 1000/(√3x415*0.8) = 1.739 Amps is this per phase ? and therefore ... 1.74 x 3 = 5.2 Amps, so i need a 6 or 10Amp breaker is needed ?

2 Answers

Relevance
  • 1 year ago

    10kW = 10/3 kW per phase = 240*i

    Phase current = 10e3/(3*240) = 13.89A so 15A breaker

  • 1 year ago

    PICK 25A CIRCUIT BREAKER FOR EACH LINE.