Yahoo Answers is shutting down on May 4th, 2021 (Eastern Time) and beginning April 20th, 2021 (Eastern Time) the Yahoo Answers website will be in read-only mode. There will be no changes to other Yahoo properties or services, or your Yahoo account. You can find more information about the Yahoo Answers shutdown and how to download your data on this help page.
Trending News
Control Systems question?
Ok, I want to understand this, I have the answer but I need to know why we got that answer, if we have a closed loop system with a given transfer function:
G(s) = 10 / (s+11)
What is the steady state output of the system when an input of:
2 cos (2t - 45)
is presented to the system.
the answer I have is 1.79 cos (2t - 55.3)
Please Explain, Thanx in advance.
2 Answers
- schmisoLv 71 decade agoFavorite Answer
Let x(t) be the input and y(t) be the output of the system and X(s) and Y(s) be the corresponding Laplace transforms.
The transforms are related by:
Y(s) = X(s) · G(s)
To find y(t) transform x(t) insert the expression to this equation and obtain y(t) from the inverse transform of Y(s)
x(t) = 2 · cos(2t - 45°)
= 2·cos(2t)·cos(- 45°) - 2·sin(2t)·sin(- 45°)
= 2·cos(45°) · cos(2t) + 2·sin(45°) · sin(2t)
= √2 · cos(2t) + √2 ·sin(2t)
From the transformation table you get the transform:
X(s) = √2 · s/(s²+4) + √2 ·2/(s²+4)
= √2 · (s + 2)/(s²+4)
The Laplace transform of the answer of the system is:
Y(s) = X(s) · G(s)
= 10 · √2 · (s + 2) / [(s²+4)·(s+11)]
expand to partial fractions
= A/(s+11) + B·s/(s²+4) + C·2/(s²+4)
with
A = -18·√2 / 25
B = 18·√2 / 25
C = 26·√2 / 25
Take the inverse transform from the table:
y(t) = A·e^(-11t) + B·cos(2t) + C·sin(2t)
The first term vanishes for large t, hence the steady state solution is
ys(t) = B·cos(2t) + C·sin(2t)
You can rearrange this to
ys(t) = D·cos(2t + φ)
by
D·cos(2t + φ ) = D·cos(φ )·cos(2t) - D·sin(φ)·sin(2t)
Compare the coefficients
B = D·cos(φ)
C = -D·sin(φ)
Hence
D = √(B² + C²) = √[(18² + 26²) ·2 / 252]
= √(16/5) = 1.78885
φ = arctan(-C/B) = - arctan(C/B)
= -arctan(13/9)
= -55.3°
=>
ys(t) = 1.78885 · cos(2t - 55.3°)
Note:
The argument of cosine in the input function need to be in degrees, because if you take the argument in radians, you get a wrong result for φ.
Edit:
Control engineers would take a different way to the solution.
The Laplace transform is not only a nifty mathemathecal tool, the transfer function describes the properties of the system in the frequency domain. The transfer function of the complex argument j·ω gives you the response to a sinussidoil input of frequency ω.
By evaluating the magnitude of transfer function, you get the ratio of the output amplitude to the input amplitude. The angle of the value for the transfer function in the complex plane is the phase shift between inpout and output.
For this problem:
G(j·ω) = 10 / (11 + j·ω) = 10· (11 - j·ω) / (11² - (j·ω)²)
= (11 - j·ω) ·10/(11² + ω²)
The magnitude is the square root of the squares of real part and of imaginary part::
|G(j·ω)| = √(11² + ω²) ·10/(11² + ω²) = 10/√(11² + ω²)
The angle in the complex plane is the inversetangent of the ratio imaginary part to real part:
φ = arctan(-ω/11) = -arctan(ω/11)
For an input function with ω = 2 and amplitude x_max=2
=> x = 2sin(2t)
The amplitude ratio is
y_max / x_max = |G(j·2)| = 10/√(11² + 2²) = 10/√(11² + 2²)
= 10 / √125
<=>
y_max = 20/√125 = 4/√5 = 1.78885
The phase shift is:
φ = - arctan(2/11) = -10.3°
For an input function with a certain phase shift:
like x = 2sin(2t + φ_out), you get the out put phase shift from
φ_out = φ_in + φ
A cosine input function is nothing else that a phase shifted sine function. Hence it will behave similar.
For
x(t) = 2cos(2t - 45°)
=>
y_max = 4/√5
φ_out = -45° - 10.3° = -55.3°
and
ys = (4/√5) · cos(2t - 55.3°)
- 4 years ago
the blunders to which you referr to is termed offset. An On/Off administration is by making use of no capacity in a gradual state as its administration sign is the two On or Off and therfore motives the innovations-set value to continuously be in the two an up style or down style. Proportional systems generate a administration sign (corrective action) it somewhat relies on the quantity of deviation from set ingredient (the quantity of blunders) it somewhat is extra approximately by making use of making use of a replace in kit stability (replace in load). there's a mounted relationship between the quantity of deviation and the resulting corrective administration sign which could be viewed a earnings value it somewhat is extra suitable with the deviation to compute the quantity of administration sign. This multiplier creates a proportional reaction to an quantity of deviation from setpoint. >>>Why does good state blunders take place in a proportional administration kit? <<< using actuality if the quantity of deviation ameliorations in an attempt to does the quantity of administration sign. Its like a weigh being placed on a spring. Initally it bounces up and down and settles out with a huge-unfold compression for a given quantity of load (weight) . If the spring attempts to return to its unique lenght much less stress is generated to counter the load. for this reason the spring keeps to be compressed jointly as a weigh is placed on it. The proportional kit reponds to boot the place the quantity of deviation creates a proportional administration respnse for a given load. save the load an identical and attempt to alter the quantity of deviation and additionally you to boot mght replace the quantity of administration sign. On Off administration differs in that there by making use of no capacity a genuine stability acheived between load and the administration and teh kit is operated indoors a suited deadband selection of PV.