Yahoo Answers is shutting down on May 4th, 2021 (Eastern Time) and beginning April 20th, 2021 (Eastern Time) the Yahoo Answers website will be in read-only mode. There will be no changes to other Yahoo properties or services, or your Yahoo account. You can find more information about the Yahoo Answers shutdown and how to download your data on this help page.

Anonymous
Anonymous asked in Home & GardenDo It Yourself (DIY) · 10 years ago

AC motor single phase trips RCD?

Ive got a really old mini lathe with its own AC motor 240v. The motor is single phase, capacitor start and 1/3hp. The motor drives the lathe via a belt and counter shaft system. Sometimes when I turn the motor on, it trips the household RCD (30a), this seems to happen most on startup or when under load. Does anyone know what is likley wrong? If I disconnect the belts the motor seems to run fine without tripping the rcd. IM guessing the extra load at startup or cutting is causing some kind of electrical imbalance. How can I test the motor? I have a multi meter. All info welcome

8 Answers

Relevance
  • 10 years ago
    Favorite Answer

    I think you mean a 30mA trip RCD (earth trip). If there is an imbalance of current, usually due to an earth fault, in the live and neutral conductors of a circuit the RCD will detect this and switch off (trip).

    There may not be anything wrong with your motor. Capacitor start motors can occasionally trip ordinary RCDs, usually when its centrifugal switch switches the starting winding and capacitor, which can give an imbalance for a fraction of a second due to the charging / discharging of the capacitor, or possibly a dirty / faulty centrifugal switch. I come across this occasionaly with single phase capacitor start motors in industrial type equipment, pressure washers and floor polishers etc, but rarely is it a motor fault. If in doubt, contact a local electrician or motor repairer to carry out an insulation test on it and advise, as a multimeter may not pick up an insulation fault. If the motor is found to be O/K and the RCD tripping is a real pain, a possible "cure" may be to install a separate circuit for the motor and protected by a time delayed RCD.

    Hope this helps.

    Source(s): Electrician and appliance repairer.
  • 5 years ago

    This is probably a split phase capacitor start motor where all or part of the capacitance used in starting is switched out once it is running, and that would be the first place I would have looked as you have done. The rcd rating is about 12 times the full load current and this would not protect it against an overload, so it sounds like there is a fault in the motor or the feed to the motor and the only way to find it is to take the circuit apart and do insulation checks on each bit. Intermittent faults like this are hard to find as when a test is carried out the fault doesn't always show.

  • ?
    Lv 5
    10 years ago

    RCD's will only detect earth faults, not over-current faults and they are rated in milliamps (mA). I feel that your protective device may be an MCB however this would be 32A and not 30A, whatever I think you have an inrush over-current causing nuisance tripping.

    Type C MCB's are designed to deal with small inrush currents such as this and I suspect yours is a Type B. I feel the answer is to protect your lathe with a local Type C MCB of an appropriate rating in line with discrimination requirements - which means it must be of a smaller rating than the next breaker upstream. If you have a Type C MCB then the rating is incorrect and needs a higher one, ie 40A.

    If I'm wrong and your lathe is plug in and it is a 30mA RCD that is 'tripping' then you have an earth fault in your motor, which is nothing to do with overload or inrush currents.

    EDIT: As an afterthought, just to be clear, your house should never be plunged into darkness because of a dodgy motor. If you have a fault on your kettle you expect the plug top fuse to blow, not the household RCD! Thats what I mean by discrimination, every appliance and conductor (cable) needs a correctly rated protective device.

  • Jim W
    Lv 7
    10 years ago

    Remove the motor and have it serviced. I suspect that it needs to have all of the wood shavings removed and new bearings installed. 1/3 HP should not trip a 30 amp breaker unless there is more on the circuit. This small motor should never be started under load. It should be allowed to come to full speed before the load is applied. Use an idler pulley to do this.

    Source(s): 50+ years in the electrical industry. Also got a wood lathe.
  • How do you think about the answers? You can sign in to vote the answer.
  • Anonymous
    7 years ago

    In the event that you need to discover pleasant thoughts for woodworking I can propose you to check here http://woodworking.toptips.org/

    It's perfect in the event that you are simply starting out or in case you're a prepared carpenter.

    It has thousands and thousands of woodworking arrangements and you have a CAD/DWG software to view and alter the arrangements. You have regulated instructions with photographs and excellent blueprints and schematics. On the off chance that you are a beginner this is the simplest approach to start your woodworking projects, and on the off chance that you already have experience you can at any rate discover a ton of interesting thoughts!

  • Anonymous
    7 years ago

    If you have to find nice ideas for woodworking i can suggest you to check here http://woodworking.toptips.org/

    It's perfect if you are just starting out or if you're a seasoned carpenter. you will like it for sure !

    It has almost 20.000 woodworking plans and you have a CAD/DWG software to view and edit the plans. You have step-by-step instructions with photos and high quality blueprints and schematics. If you are a beginner this is the easiest way to start your woodworking projects, and if you already have experience you can anyway find a lot of interesting ideas!

  • 10 years ago

    An RCD is for current overloads - not unequal currents so it is overloading. This is not particularly dangerous. There is nothing wrong other than you are overloading a little motor. Put a trip near the lathe so as you don't have to hurry to the basement each time it goes.

  • Anonymous
    10 years ago

    You have more than your lathe running on that electrical circuit...go turn the breaker off and see what else goes off.