Yahoo Answers is shutting down on May 4th, 2021 (Eastern Time) and beginning April 20th, 2021 (Eastern Time) the Yahoo Answers website will be in read-only mode. There will be no changes to other Yahoo properties or services, or your Yahoo account. You can find more information about the Yahoo Answers shutdown and how to download your data on this help page.

Calling all AC technicians. Are low pressures the only way to determine Refrigerant?

I charged my 2.5 ton system with 12 oz in May, 1lb 12oz in Sept and 1 lb 2 days ago.

I found A leak with a leak detector in the suction line service valve. It was not tightened down enough.

The pressures now with a 75 degree ambient are 55 and 200 psig and so the Evap is freezing up

The wetbulb is 64-66.

+ so, I don't want to overcharge it since I've put in 3 lbs and 8oz already and it holds 4.5 lbs with a 25 foot + lineset.

So I want to know if I can count on the L and H pressure readings telling me that the system is still low and needs more refrigerant.

Thanks.

epa liscenced universal

Update:

Well, just found a leak at the condenser where the suction line is brazed to the access valve. And the LL valve cap was loose.

And, my hoses leak like crazy. \

Got some new ones and will try charging again.

Update 2:

I didn't figure on bad gauages and leaky service caps, not the service ports. Ports were ok. It is holding now at 73 suction; 260 liquid, 85-90 ambient. Added 12 oz.

Amazing how almost the whole charge could leak out since May.

It was vibration that loosened the caps.

I panicked because I thought of everything but that.

1 Answer

Relevance
  • manny
    Lv 5
    8 years ago
    Favorite Answer

    I'm not an expert, but I was told to compare the air as it leaves the vent with the air in the room. The difference should be 18 degrees or somewhat lower. It works for me.