Yahoo Answers is shutting down on May 4th, 2021 (Eastern Time) and the Yahoo Answers website is now in read-only mode. There will be no changes to other Yahoo properties or services, or your Yahoo account. You can find more information about the Yahoo Answers shutdown and how to download your data on this help page.

?
Lv 6
? asked in Home & GardenMaintenance & Repairs · 7 years ago

Do I have a serious electrical wiring issue?

I plugged in a computer to one of my outlets. I felt current passing through my band as I touched the case and held the monitor Connection and got a big spark when I tried to connect the monitor. This only happens on that outlet. I took the outlet out to see if the problem was obvious and heres what I saw. ) here's an image to help illustrate what i'm describing...

http://completeelectrical.biz/wp-content/uploads/2...

There was no red wire (I know this is normal) but what I saw was the ground wire was not connected but present and there was a wire connecting the Common connectors to the ground connectors.

I've been using the outlet just fine for years and still am as it currently has my modem and router.

My question is, us this a serious problem that I need to address before I catch fire? Or, is this something that I can fix eventually?

Also, Is that wiring actually ok or does this sound like I have a bad wire in the wall?

I tried to remove the common-ground connection and hook up the ground wire in its place but the outlet no longer worked.

5 Answers

Relevance
  • 7 years ago
    Favorite Answer

    You need an electrician to sort this out, as you have probably tripped the breaker or blown a fuse.

    You don't know enough to solve this if someone else wired the rest of the circuit wrong.

  • KMA
    Lv 6
    7 years ago

    The neutral wire is not working and someone used the ground to "make" the receptacle work. It's not correct and as you see not particularly safe. That's why when you put the wires where they are supposed to be the outlet stopped working.

    Turn off the power and go box to box inspecting the wires, splices and connections at all other outlets on this circuit. Hopefully you will find and fix the reason the neutral doesn't work. If your outlets have the wires pushed into the back, pull them out and wrap them clockwise around the screws.

    If after that the neutral still doesn't work then the wire is damaged somewhere between boxes and fixing that can be anything from moderately difficult to impossible without removing baseboards, crawling under the house or through the attic.

    Source(s): licensed electrician
  • Anonymous
    7 years ago

    The diagram you show is for a split receptacle where one outlet is hot at all times while the other is controlled by a switch. This is why the tab on the right has been removed. The tab one the left is retained in order for both outlets to share the neutral wire. Since you say that the red wire is not present in your case this does not apply. If you only have two conductors and a ground coming in to the electrical box, this is the end of a circuit. The bare ground wire should be attached to the ground terminal. The white neutral wire should be attached to the terminal with the silver terminal and the hot black wire should be attached to the darker or brass colored terminal. Once this is done the receptacle should function properly. If it does not, replace it.

  • Jim W
    Lv 7
    7 years ago

    It sounds like you need to replace the outlet and before you are done you will need some special tools. A receptacle tester about $5 US and a screwdriver and some wire strippers or a knife to remove the insulation. Do not use a back wire type. The device wiring indicates to me that you have an open neutral in the circuit and it may be in another outlet that needs to be inspected. The receptacle tester will help. you locate the problem area. The wiring is seldom damaged in the wall rather usually in a device box.

  • ?
    Lv 6
    7 years ago

    It sounds like there is power on the ground wire you can try to use a grounding adapter to break the ground path to see if this helps if that fixes the problem then call a electrician or fix it if you know how. The common and ground should be a separate connection.