Yahoo Answers is shutting down on May 4th, 2021 (Eastern Time) and beginning April 20th, 2021 (Eastern Time) the Yahoo Answers website will be in read-only mode. There will be no changes to other Yahoo properties or services, or your Yahoo account. You can find more information about the Yahoo Answers shutdown and how to download your data on this help page.

How do I calculate arc flash rating?

How do calculate arc flash rating?

I 208/120 volt panel with a short curit current of about 13,000 amps. How many calories per cm^2 of energy does this create. And how do I calculate this?

Update:

This panel is fed with a 400 amp Molded case breaker

1 Answer

Relevance
  • 1 decade ago
    Favorite Answer

    First you need to get your hands on an Arc-Flash Incident Energy Calculator. It is a chart. One place I know that has one is the Bussmann, Handbook for Electrical Safety, Editiion 2. Appendix G.

    Just looking at the chart it looks like the incident energy value is between 0.96 to 1.11 cal/cm^2 for a 1 to 100 amp molded case circuit breaker. The Flash Protection Boundary is 15 to 17 inches.

    You really need to look at the chart. I don't see an adjustment for voltage, just fault current, and the fault interuption device, various fuses and molded case circuit breakers.