Yahoo Answers is shutting down on May 4th, 2021 (Eastern Time) and beginning April 20th, 2021 (Eastern Time) the Yahoo Answers website will be in read-only mode. There will be no changes to other Yahoo properties or services, or your Yahoo account. You can find more information about the Yahoo Answers shutdown and how to download your data on this help page.

?
Lv 5
? asked in Science & MathematicsEngineering · 1 decade ago

In Star Connection meeting point of 3 phases is taken as earthing or ground,but what of Delta circuits?

Electrical energy :in transmission,Generation & distribution,how is grounding/Earthing point for delta circuit determined?

1 Answer

Relevance
  • 1 decade ago
    Favorite Answer

    There are a few common techniques for grounding a delta system. These are:

    1. Leave it ungrounded, so the only ground connection is through parasitic capacitance of the system. It is common to apply some form of voltage-based ground fault monitor on this system, since a phase-to-ground fault causes vary little current flow.

    2. Connect one phase to ground, then use two conductors to distribute the other two phases. This is referred to as a 'corner grounded' system. It is still a three-phase system.

    3. Use a transformer with midpoint tap. Ground the midpoint tap. In the U.S., this is seen as 240V delta, with 2x 120V from the transformer winding with the midpoint tap.

    4. Apply a separate grounding transformer, such as a zigzag or wye-delta, with or without additional impedance in the neutral to limit ground fault current.

    Source(s): As an electric power engineer, I've dealt with all of the above.