Yahoo Answers is shutting down on May 4th, 2021 (Eastern Time) and beginning April 20th, 2021 (Eastern Time) the Yahoo Answers website will be in read-only mode. There will be no changes to other Yahoo properties or services, or your Yahoo account. You can find more information about the Yahoo Answers shutdown and how to download your data on this help page.
Trending News
shopping mall electricity?
about how many amps does a large shopping mall use?
2 Answers
- Thomas CLv 61 decade agoFavorite Answer
The actual load of a commercial customer is substantially less than the size of their main switch. Usually far less than 50%.
It is hard to define a "large shopping mall", so here are some numbers that will put things into perspective.
A 120,000 ft² retail store (ex. Walmart, Target, etc) has a peak summer demand of around 500-600 kW. More for a Supercenter.
A slightly smaller retail store (ex. Kohl's) is probably around 250 kW.
Small stores in the mall are in the 30-50 kW range.
A 70,000 ft² grocery store will have a peak summer demand of around 700-800 kW.
A large shopping mall with multiple anchor tenants might be in the range of 3 to 4 MW. (3000 to 4000 kW)
Malls generally take electric service at 277/480 3-phase. Assuming a power factor of 0.90, you can convert kW to amps, with the following formula.
kW ÷ 0.90 ÷ .480 kV ÷ √3 = amps
Simplified: kW ÷ 0.747 = amps
>>>>>>>>>>> UPDATE <<<<<<<<<<<
I obtained some actual loads on a 4,000,000 ft² shopping mall served with a spot network. The summer peak load for the entire mall is 13,700 kW. That works out to around 3½ watts per ft².
>>>>>>>>>>> UPDATE <<<<<<<<<<<
- EdesignerLv 61 decade ago
Roughly the average mall will have a 2000amp service ...This may be in the form of a combination of service drops ranging in size from 225amps to 400amps the most common voltage at the amperage is a 480/277 3phase 4 wire wye.....120 volt power is aquired from transformers within the system.....from the E...