Yahoo Answers is shutting down on May 4th, 2021 (Eastern Time) and beginning April 20th, 2021 (Eastern Time) the Yahoo Answers website will be in read-only mode. There will be no changes to other Yahoo properties or services, or your Yahoo account. You can find more information about the Yahoo Answers shutdown and how to download your data on this help page.

SFB asked in Science & MathematicsEngineering · 1 decade ago

How to deliver 450KW of power?

This is a followup to this question:

http://answers.yahoo.com/question/index?qid=201009...

Which is presumably a homework assignment to find out how much power it would take to heat a swimming pool in 2 hours. The answer is 450KW

Assuming that you really did want to install this high powered pool heater, how would the power company deliver 450KW? Even 480V service would require 1000A of current -- what's the standard service voltage above 480V?

Update:

What size wire do they deliver 800 amps on? The biggest size that I know of is OOOO (4/0), but it's only rated around 300 - 482 amps open air current. Is there a OOOOOOO (7/0) wire gauge?

I know the power companies aren't subject to normal NEC regulations, so maybe they can deliver power over smaller wire?

2 Answers

Relevance
  • Gone
    Lv 6
    1 decade ago
    Favorite Answer

    Parallel conductors are used to supply current when the largest available conductor is not large enough or when two or three smaller conductors are more convenient to install. There are also busway products that carry current using copper or aluminum bars enclosed in a metal duct.

    Above 480 volts, standard utilization voltages are 575 volts, 2300 volts and 4160 volts in the USA and Canada. In the USA, 575 volts is not used very much, but it is used in preference to 480 volts in Canada. Users of voltages of 480 volts and higher would generally be supplied 3-phase power from a transformer located on the customer's property. Either the utility or the customer might own the transformer.

  • 1 decade ago

    It varies. It depends on what is available in the street near you, on on the poles. Usually about 6kV. But I don't think you have to go above 480.

    My condo building has 120/208 3 phase at 800 amps per phase, or a total of 288 kW

    A 277/480 volt 800 amp 3 phase service would deliver 664 kW, easy to do. And most commercial heavy equipment can be bought setup for 480 volts, or 277 volts.

    .