Yahoo Answers is shutting down on May 4th, 2021 (Eastern Time) and beginning April 20th, 2021 (Eastern Time) the Yahoo Answers website will be in read-only mode. There will be no changes to other Yahoo properties or services, or your Yahoo account. You can find more information about the Yahoo Answers shutdown and how to download your data on this help page.
Trending News
Here is one for you electricians out there. What is the problem?
I have two bedrooms in my house that have lost power. The circuit that they are on is with the rest of the back of the house that has not lost power. Only the two rooms. Could it be a switch or corroded connection is a wall socket? I have had problem that took out the whole circuit but not just two rooms due to bad connections.
Could this be just be some bad connections between the two rooms?
2 Answers
- Steven JLv 710 years agoFavorite Answer
Most likely it is a lost neutral wire.
Check where the electricity is still flowing in the outlets and look for a neutral wire splice. It is most likely the problem.
Without a neutral wire the current does not flow as needed back to the circuit breaker.
Another words the hot wire could be live from the electrical panel. And a tick tester or proxiamaty sensor will sense it.
Corroded switches or outlets only increase the resistance. But not enough to stop electrical flow per ohm's law.
Plus corrosion would only come into effect if the wire terminals are loose.
Source(s): Union Electrician, local 134, Chicago, IL. Lost neutrals are are a big problem in power loss from damaged cords or wires. Many electrical devices can still say the hot wire is electrified. But require a voltmeter or plug tester to show a lost neutral. Ohm's law where Voltage = current times resistance. - 10 years ago
Has one of the rooms that has lost power have a GFCI receptacle? If so remove and replace it or wire around it to check for the problem.