Yahoo Answers is shutting down on May 4th, 2021 (Eastern Time) and beginning April 20th, 2021 (Eastern Time) the Yahoo Answers website will be in read-only mode. There will be no changes to other Yahoo properties or services, or your Yahoo account. You can find more information about the Yahoo Answers shutdown and how to download your data on this help page.

Ventilation for room protected by FM200?

Is a room that is protected by FM200 should need to provide ventilation to exhaust the agent after discharged. If yes what should be the air change for this particular application.pls help.tnx!

1 Answer

Relevance
  • 10 years ago
    Favorite Answer

    23. Is there any post-activation purge/ventilation requirements for your system?

    There is no requirement within NFPA 2001 for a dedicated exhaust system when using DuPont™ FM-200®. NFPA requires that the post-extinguishment atmosphere be ventilated in a safe manner. With most installations, this can be accomplished by simply turning on the air handling units and allowing enough time to dissipate any smoke in a post-fire event.

    Some jurisdictions have implemented additional local requirements concerning ventilation systems. You should check with your local authorities.