Yahoo Answers is shutting down on May 4th, 2021 (Eastern Time) and beginning April 20th, 2021 (Eastern Time) the Yahoo Answers website will be in read-only mode. There will be no changes to other Yahoo properties or services, or your Yahoo account. You can find more information about the Yahoo Answers shutdown and how to download your data on this help page.

?
Lv 6
? asked in Science & MathematicsEngineering · 9 years ago

electrical engineering transformer problem?

A 500 KVA transformer has a 0.6 lagging power factor load of 280 KVA. (a) If additional 0.8 power factor lagging loads are to be added, how many KVA of such loads can be added without overloading the transformer? (b) A 0.8 lagging power factor load of 300 KVA is to be added. Will the transformer be overloaded? (c) If the answer to (b) is yes, determine the KVAR of capacitors needed to reduce the load on the transformer to its rated value.

Update:

In (b), please answer this portion providing a solution that will support your answer. Thanks!

4 Answers

Relevance
  • 9 years ago
    Favorite Answer

    A) 280 KVA at 0.6 power factor is 168 KW The KVAR for this load is Sqrt(280^2 - 168 ^2) = 224 KVAR

    B) 300 KVA at 0.8 power factor is 240 KW.

    The KVAR for this load is Sqrt(300 ^ 2 - 240 ^ 20) = 180 KVAR.

    The KW of the original load plust the KW of the 300 KVA load is 168 + 240 = 408 KW.

    The KVAR of both these loads is 224 + 180 = 404.

    This means the KVA of the total load is Sqrt(KW ^2 + KVAR ^ 2) = Sqrt(408 ^2 + 404 ^2) = 572.77 KVA

    The transformer will be overloaded.

    C) The KVAR required to limit a the KVA of a transformer to 500 KVA, with the KW load of the transformer being 408 KW is KVAR = Sqrt(500 ^2 - 408 ^2) = 289 KVAR. The KVAR of the required capacitor is 404 - 289 = 115 KVAR

    TexMav

  • JohnB.
    Lv 5
    9 years ago

    Power factor is defined as the ratio of real power to apparent power.

    (a) Apparent power must not exceed 500 KVA. Apparent power of the additional load must not exceed 500-280KVA.

    (b) Since the apparent power will be 280+300 KVA the total apparent power will be 580 KVA. That sounds overloaded to me.

    (c) Since "inductors are said to consume reactive power and capacitors are said to supply it" the inductors of the example are consuming 80 KVAR then the capacitors must supply supply 80 KVAR to reduce the load to rated value.

    Source(s): Wikipedia
  • Anonymous
    9 years ago

    texasmav is right, here is the situation

    before the capacitor installed

    kva ------------ kw ----------- kvar

    m|_x -----------m*cos(x)--- m*sin(x)

    280|_53.13---168 ---------- 224----------load#1

    300|_36.87--- 240---------- 180----------load#2

    574|_44.72--- 408---------- 404---------- total

    pf = cos(x) = 0.71

    574 > 500kva transformer overloaded

    kvar = sqrt(500^2 - 408^2) = 289

    capacitor kvar = 289 - 404 = - 115

    after the capacitor installed

    kva ------------ kw ----------- kvar

    m|_x -----------m*cos(x)--- m*sin(x)

    280|_53.13---168 ---------- 224----------load#1

    300|_36.87--- 240---------- 180----------load#2

    capacitor load ----------- (- 115)

    500|_35.31--- 408---------- 289---------- total

    pf = cos(x) = 0.82

    load 500 = transf 500kva

    the pf is improve from 0.71 to 0.82 after the capacitor is installed

  • ?
    Lv 4
    4 years ago

    electric powered engineering is in many situations deals with the learn of electricity, electronics, and electromagnetism.electric powered engineers artwork in an exceedingly enormous determination of industries and the abilities required are likewise variable. those variety from effortless circuit theory to the administration skills required of challenge supervisor. The approaches and equipment that somebody engineer might decide for are in addition variable, beginning from an effortless voltmeter to an excellent end analyzer to state-of-the-paintings layout and production application.