Yahoo Answers is shutting down on May 4th, 2021 (Eastern Time) and beginning April 20th, 2021 (Eastern Time) the Yahoo Answers website will be in read-only mode. There will be no changes to other Yahoo properties or services, or your Yahoo account. You can find more information about the Yahoo Answers shutdown and how to download your data on this help page.

Would you put a GFCI outlet on a circuit protected by a GFCI breaker?

If you had a single pole 20A GFCI protected circuit breaker in your panel, feeding one single 20A outlet outside in your garden (about 70 feet from the house), all enclosed in underground PVC conduit with a weatherproof device box, would you have to install a GFCI protected outlet or could you install a regular one?

5 Answers

Relevance
  • 9 years ago
    Favorite Answer

    Would not need to be gfci, but NEC 406.8 does now require it to be rated "weather resistant".

    Source(s): Local 46 Electrician
  • Jim W
    Lv 7
    9 years ago

    No you do not need a gfci outlet. If you make the mistake of installing one you will have a serious problem with nuisance tripping and the solution is to use only one device not both.

    Source(s): 50+ years in the electrical industry.
  • XTX
    Lv 7
    9 years ago

    === if you are worried about it then it is wise to use the GFCI both places == especially in the garden where you are watering the plants and you have wet feet == eliminate possible problems ...

  • Anonymous
    9 years ago

    toss that gfci breaker as far as you can and replace it with a regular breaker and put in a gfci outside.

  • How do you think about the answers? You can sign in to vote the answer.
  • Asoka
    Lv 5
    9 years ago

    Just use a regular outlet. There's no use in protecting it twice and making it hard to trouble shoot if they both blow.

    Source(s): electrician