Yahoo Answers is shutting down on May 4th, 2021 (Eastern Time) and beginning April 20th, 2021 (Eastern Time) the Yahoo Answers website will be in read-only mode. There will be no changes to other Yahoo properties or services, or your Yahoo account. You can find more information about the Yahoo Answers shutdown and how to download your data on this help page.
Trending News
How many breakers in a 100amp sub panel?
I am adding a 100 amp sub-panel. I need up to three 30amp breakers and of right this moment I need eight 20amp breakers (I STRONGLY believe 15amp breakers are a waste of time and money and should never be allowed in residential use) In future I will need four breakers for backyard, two for front yard and three for holiday specific uses. The panel is being fed by a 50amp breaker from the main 200amp. The subpanel will have either 20 slots, 20 circuits or 30 slots 30 circuits.
My question is on the amount of volts in the breaker. Up to sixteen 20 amp breakers and three 30 amp breakers plus the feed, is this too much for a sub-panel?
and yes I know the neutral and ground have to be isolated.
Thanks
No one really reads the questions do they?
I am NOT using 15amp breakers.
Yes I know wire size
The feed size is listed
The use is listed Lighting and outlet no heavey watt loads
Yes I know how to use a double pole breakers
srry but none of those answers are the questions I asked.
5 Answers
- Anonymous9 years agoFavorite Answer
You are not getting the answer you want because you are working in an area that you don't have enough knowledge to use the right terms to get the answer you need.
Any panel smaller than the main is acceptable for a sub panel.
The capacity of the panel will be determined by the weakest link.
The weakest link you described is the 50 amp breaker.
Any sub panel must be rated at least the breaker feeding it.
Choosing a 60, 100, or 200 amp panel will not increase capacity
All breakers will always feed either 120 or 240v.
Volts don't go up or down when used.
Amps are determined by dividing watts by volts.
Amps get added to determine load.
Load diversity is the determination of coincidental loads.
Load diversity decides the needed ampacity of panel.
Without knowing the loads, nobody can tell the size needed. I can't imagine how 50 amps would be enough to describe the number of circuits you described. I bet you would need a 100 amp breaker in the main panel, #2 awg feeders to a 100 amp subpanel with at least 30 full size spaces. Most 20 space panels do allow 1/2 space breakers making a 20 space panel capable of 40 circuits, but there is no reason to kick yourself in the XXXXX right out the front door.
- c_kayak_funLv 79 years ago
Not enough information. You don't state what your loads are. Your sub feeder size and the number and size of circuits you require have to be based on the loads you expect and whether they can be derated.
Unless we know the load ampacities, no answer to your question would be valid, so ignore what has been posted so far.
Voltage is not the issue here, it is watts and amps. Also, I hope that you are planning to use all 12 gauge wire with these 20 amp breakers that you prefer. You do know that wire gauge has to be matched to the circuit protection. I suspect your 50 amp feeder to the subpanel may be inadequate as well. Again, can't answer that in an informed way without more detail from you.
Source(s): Licensed electrician for 32 years and electrical inspector for 25. - Jim WLv 79 years ago
Twin breakers for the 20 amp circuits should allow what you want to do. These put 2 breakers in the space that is usually for 1 circuit. Go to the electrical supply section of the online retailers and research the panel sizes.
Source(s): 50+ years in the electrical industry - How do you think about the answers? You can sign in to vote the answer.
- JrbottLv 69 years ago
Really depends on the panel purchased. If you were to use 15 amp breakers you could have 100/15= lines, so you would need that many openings in the box plus a couple spares. Just do the math....