Yahoo Answers is shutting down on May 4th, 2021 (Eastern Time) and beginning April 20th, 2021 (Eastern Time) the Yahoo Answers website will be in read-only mode. There will be no changes to other Yahoo properties or services, or your Yahoo account. You can find more information about the Yahoo Answers shutdown and how to download your data on this help page.
Trending News
Gas furnace won't kick back on, pilot light still on?
Turned down the thermostat, turned up back up a few hours later. Furnace won't make a sound, won't kick in at all. Pilot light is still on. Replaced thermostat, and still nothing. It's a Rheem propane furnace.
The thermostat was really old. It was a 2-wire heat only, so it was a quick install. But the problem happened before we replaced the old thermostat. Power is on, pilot light is still going.
Plenty of propane. 65%
7 Answers
- Propane GuyLv 78 years agoFavorite Answer
Man...oh man...the answers I see on here.
The first thing to do is jumper the thermostat connections (temporarily) on the gas valve and see if the furnace kicks on.
If it fires up you either have a bad t-stat or it is wired incorrectly.
If it doesn't start up then you'll probably need a qualified technician to diaqnose the furnace for you. There is flame safeguards, proving circuits etc that you won't be able to diagnose properly yourself.
If you do try and diagnose it yourself, you will probably end up spending more money throwing parts at it than if you paid a technician in the first place.
Good luck with it!
Source(s): 25 years experience in the propane business and a licenced gas fitter - papawLv 78 years ago
So, turn the thermostat down even more, with a new one, you might need to go lower than you think to get it on. Are you sure you have put the furnace back into automatic mode, and not manual?
Papaw
- Greg DLv 58 years ago
Without diagnostic info your guess is as good as mine.
Possible problems:
Blown fuse
Dead transformer
Switch/power is off
Furnace blower door safety switch is not closed
Bad circuit board
Shorted wire
Bad gas valve
Bad ignition control
Loose wire
Open high limit
Open roll out.
If it has one, a bad inducer motor
Source(s): HVAC/R Service Tech - 8 years ago
Have you checked to see if you have 24 volts? If you don't it sounds like a transformer. If you do then check to see if you have 24 volts to the gas valve. If you do then the gas valve is bad. If you have 24 volts at the transformer and not at the gas valve then you have a safety tripped. Good luck.
Source(s): HVAC contractor - How do you think about the answers? You can sign in to vote the answer.
- William BLv 78 years ago
Why did you replace the thermostat? was it bad ?
did this happen before you replaced it or after ?
did you shut the electricity off to it ?
did you forget to turn it back on ?
Source(s): maint man - Anonymous8 years ago
kick it again