Yahoo Answers is shutting down on May 4th, 2021 (Eastern Time) and beginning April 20th, 2021 (Eastern Time) the Yahoo Answers website will be in read-only mode. There will be no changes to other Yahoo properties or services, or your Yahoo account. You can find more information about the Yahoo Answers shutdown and how to download your data on this help page.

?
Lv 4
? asked in Science & MathematicsEngineering · 8 years ago

4 wire, unbalanced star load. Please help me!?

I'm quite stuck on an assignment.

400V, 3 Phase supply, 4 wire star, 3 resistive loads of - 24kW, 18 kW, 12kW.

I need to find out the current in each line and the current in neutral conductor.

Any help on what I need to do, would be soooo great!

Thankss.

2 Answers

Relevance
  • 8 years ago
    Favorite Answer

    400 volts phase to phase is 231 volts phase to neutral.

    Assuming the loads are connected phase to neutral, then the currents are

    24 kw/231 = 104 amps

    18 kw/231 = 78 amps

    12 kw/231 = 52 amps

    we can add these as vectors to get the current in neutral

    104 amps = 104i

    78 amps = –78isin30 + 78jsin60 = –39i + 67.5j

    52 amps = –52isin30 – 52jsin60 = –26i – 45 j

    sum is 39i + 22.5j

    magnitude is √(39² + 22.5²) = 45 amps

    but check the math

  • 8 years ago

    Voltage per phase = 400/sqrt(3) =235 v/ph

    P = V x I x pf

    pf is unity for resistive loads.

    Therefore,

    I1 = 24000/235 = 102.13 A

    I2 = 18000/235 = 76.6 A

    I3 = 12000/235 = 51 A