Yahoo Answers is shutting down on May 4th, 2021 (Eastern Time) and beginning April 20th, 2021 (Eastern Time) the Yahoo Answers website will be in read-only mode. There will be no changes to other Yahoo properties or services, or your Yahoo account. You can find more information about the Yahoo Answers shutdown and how to download your data on this help page.

Welder amps?

I recently got a new welder, it’s a titanium unlimited 200 which for stick welding is rated for 200a but when I turn the knob it only goes to 170. It’s running on an extension cord that’s about 100ft but I checked the voltage at the welder end and it still says 240v. I know it should be able to do 200a cause all the charts on it with the recommended amps for each electrode go that high and some go to 210a and even the duty cycle is rated at 200a. What could be limiting it, is there something I’m doing wrong? I’m gonna be doing a build soon with some 5/32 7018 on some pretty heavy walled steel and could use the extra amps

9 Answers

Relevance
  • 1 year ago

    When using welders especially stick try to use it as close as possible to the fixed power source. The time of day that you are welding can be critical as well depending on where you live and how stable your power supply is. Recommend using an independent power supply for your welder (generator). With a 200 amp welder 22amp circuit I would use nothing under 7kva. I have often switched to my portable Genset for better welding results. I hope this helps you out.

  • 1 year ago

    never run an electrical wielder on an extension cord !you will ruin it or melt the cord !

  • 1 year ago

    When the welder is running the voltage will drop to zero and the amps will raise to max.

    The core size of the supply cable could be too small. Is the cable becoming warm under load? If so, then replace it with a cable that has a larger core size E.G 2,5 cubic-square m/m per core or greater.

    Welding unites have a core saturation time called -intermittent- as the coil warms up the coil resistance increases and the amps fall. Your welding unit could be too under dimensioned for the job in hand.   

  • elhigh
    Lv 7
    1 year ago

    You check the voltage and it's still 240, but under load there's such a thing as voltage sag, and you're not testing under load.  Chances are very good that at heavy amps you're not getting anything like the full 240.

      You need a thicker cord, a shorter one, or both.

  • How do you think about the answers? You can sign in to vote the answer.
  • 1 year ago

    the voltage might say 240 volts but under load the current is dropping because of the long extension lead 

  • y
    Lv 7
    1 year ago

    More then likely the extension cord needs a larger wire size in order to allow the proper flow. Most extension cords tend to use the minimum sized wires they can get away with. Look, if possible at the gauge your extension cord uses and then find ones that can carry more.

  • 1 year ago

    The problem is most likely due to the length, and possibly the conductor sizes, of the extension cord. All wiring has a resistance which can cause a voltage drop when under load, including the house wiring. The higher the load the more the drop. Even a 5% voltage drop will give a notably reduced performance of the welder when welding. To get a true idea of the voltages you will need to get someone to check the voltage at the supply outlet / socket and the welder end of the extension cord while you are trying to weld, your multi-meter will do to check this, and if the voltage is considerably lower at the welder end of the cord  you may need to to use a larger capacity of cord or use the welder closer to the supply outlet / socket.

    Hope this helps.

  • 1 year ago

    support page at the maker's website

  • Bill
    Lv 7
    1 year ago

    Did you check the voltage while the welder was producing the maximum amps?

Still have questions? Get your answers by asking now.