Yahoo Answers is shutting down on May 4th, 2021 (Eastern Time) and beginning April 20th, 2021 (Eastern Time) the Yahoo Answers website will be in read-only mode. There will be no changes to other Yahoo properties or services, or your Yahoo account. You can find more information about the Yahoo Answers shutdown and how to download your data on this help page.
Trending News
6-3 wire in 3/4 liquid tight tubing...too much?
I am running 6-3 wire for a spa (hot tub).It will be ~12 ft run to the spa sub panel and then 15 ft to the spa. I want to use liquid tight tubing since it is a wet location (duh) and it will protect the wire. Lowes and HD only have 1/2 and 3/4 inch conduit. The wire fits inside and I can easily pull it through the short lengths needed to do the job.
My question is: Is this too much wire in too small of a conduit diameter? ie DO I have to worry about over-heating?
6 Answers
- John himselfLv 61 decade agoFavorite Answer
Yes you can.
Table C.7 Annex C of the National Electric Code allows 3 or 4 number 6 wires in a 3/4 Liquid tite flex conduit depending on the wire type. So you will be fine with 3. No problem. Good catch on the over heating. That is the reason for the restrictions on conduit fill. If you have romex, I would strip off the outer sheath for the conductors inside the conduit.
Source(s): I'm an electrician - toddrfLv 41 decade ago
For a max 40% fill, you need at least 3/4" conduit for 3x #6, so I'd say you should be fine.
- 1 decade ago
you will be ok with 3 #6 wires in 3/4 in pipe but i wouldn't run 6-3 romex in the pipe,that is what it soundl like you want to do. go to home depot and get 3 seperate #6 wires dont forget to properly ground the tub. If u have any ?'s feel free to email me.
- How do you think about the answers? You can sign in to vote the answer.
- skibm80Lv 61 decade ago
The outside wire sheath should not become hot at all, so it should be fine in the conduit.