Yahoo Answers is shutting down on May 4th, 2021 (Eastern Time) and beginning April 20th, 2021 (Eastern Time) the Yahoo Answers website will be in read-only mode. There will be no changes to other Yahoo properties or services, or your Yahoo account. You can find more information about the Yahoo Answers shutdown and how to download your data on this help page.

electric heat element amp/breaker?

I need to know what amp. contactor and feed breaker to use if building a powder coat oven using 2800 watt elements.

two elements_______________three elements__________

four elements_______________ all 2800 watt 240 volt each.

I want to heat to and maintain 450 degree.

2 Answers

Relevance
  • Anonymous
    1 decade ago
    Favorite Answer

    2800*2=5600 Watts /240= 23Amps

    2800*3=8400 Watts /240 = 35 Amps

    2800*4= 11200 Watts /240 = 46 Amps

    So you need a 30 amp braker 2phase if your panel is single phase. Feed it with # 10 wire in a 1/2 in conduit

    Also a 40 amp braker 2 phase. Feed it with #8 in 3/4 conduit

    And finaly a 50 amp braker 2 phase Feed this with # 8 wire in 3/4 conduit.

    Source(s): Electrican
  • Irv S
    Lv 7
    1 decade ago

    You will draw about 12A. per element at 240 V.

    Depending on how you arrange your controls,

    you should size your contactors for 150% of load,

    (to handle inrush currents), and your main breaker

    for 125% of the total.

    Large tungsten heaters do have an inrush and I

    would recommend you use 'motor rated' contactors.

    (I hope you're not proposing to use water heater elements.

    They would be mis-applied in an air heating application

    without some kind of radiator/heat sink.)

    Source(s): Retired Electrical Consultant