Yahoo Answers is shutting down on May 4th, 2021 (Eastern Time) and beginning April 20th, 2021 (Eastern Time) the Yahoo Answers website will be in read-only mode. There will be no changes to other Yahoo properties or services, or your Yahoo account. You can find more information about the Yahoo Answers shutdown and how to download your data on this help page.

York central AC not working right.?

Unit was installed last July. Repairmen don't seem to have a clue. First it lost it's charge but only took 3 # to fill. Next day same thing. Unit running but not cooling and coils under furnace frosted over. Original check said it lost the charge, hour later charge was fine without adding to it. Then compressor won't come on. Could this be caused by a faulty thermostat? I live in a mobile home and this is a 3 ton unit. Worked fine until 2 days ago. Any help appreciated.

Update:

Both days when they hooked the gauges up to check freon level they registered zero but only took 3# to fill first day. Second day registered zero but charge came back to normal after about 30 minutes. Still said it had a charge but not cooling and compressor failed to start.

Update 2:

Installation was July, 2008. You have the sequence right. I guess freon could have escaped but don't understand how it could have built back up. Other scenario by them is furnace fan not strong enough but was for a year. They say the unit is getting "call" because the fan is kicking on but not the compressor. Talking a full days labor to unhook something at the outside unit and check but if nothing wrong pulling the coil to unhook and check. Also, I have cats and they say that the ammonia that normally comes from litter boxes circulating around the coil could have eaten it up. That sounds preposterous to me but I'm not a tech. On the other hand the thermostat was acting hinky as in if the furnace fan was on and I bumped the wall near it it would go off. Now if it's on and I bump the wall the blower stays on. That's what has me thinking maybe it's the thermostat.

4 Answers

Relevance
  • Anonymous
    1 decade ago
    Favorite Answer

    If you aren't satisfied with the company servicing your a/c, then call someone else. A frozen coil is a symptom of low refrigerant charge, but it can also be caused by poor air flow.

  • Marko
    Lv 6
    1 decade ago

    Your system was installed last month and had a correct charge, then lost 3 lbs, then, the next day another 3 lbs., then the charge was fine ?

    Then the compressor won't start ? Don't know if that is the correct chain of events.

    Well, an under-charge will effect a compressor adversely and it will overheat and shut down. Or it will be damaged by liquid refrigerant if the system is over-charged.

    Sounds like the compressor will have to have the compression ratio

    tested to see if it has been damaged.

    And, there is a leak because of the indoor coil is freezing. The leak will have to be found and repaired.

    Is it possible that the repairmen allowed the 3 lbs. of refrigerant to escape when they were checking the system ?

    a. If the charge took 30 minutes to show up as the correct low pressure, I would suspect that the refrigerant charge is not passing through the metering device and into the evaporator as designed. They should know in 2 minutes.

    That could be because the metering device is restricted.

    It could be that the charge they put in contained air via not purging their hoses on their gages. That can cause strange readings and low cooling.

    b. The indoor fan blower motor has a run capacitor to help it operate and it may need to be replaced.

    c.You can test your thermostat by Jumping it with an insulated wire, about 4 inches long. Remove the t-stat to view the subplate on the wall. Put the wire on R on one end and Y on the other. The outdoor and indoor units should start up. Remove wire. With R on one end and G on the other the indoor fan should start up.

    If this works, then the t-stat is not working correctly. Maybe a loose wire connection.

    Source(s): ac tech
  • 1 decade ago

    if your Suction pressure was 0 then went back to normal you could have a restriction in the system causing refrigerant not to flow properly

    and since Refrigerant gas coming back from Evaporator is what cools the Compressor motor your Compressor may have been of on thermal overload to protect the compressor from burning up if the compressor comes back on after sitting for an hour or two then it was more than likely offf on overload and the other post were Correct I would not let that AC tech or Company back in your yard that should have been repaired first trip out

    Source(s): 28 years in the AC business
  • Foggy
    Lv 5
    1 decade ago

    Might be a bad breaker or it could be the unit has a blockage of some sort in the sealed system or both. It might be that a critter crawled into the contactor and screwed the whole works up.