Yahoo Answers is shutting down on May 4th, 2021 (Eastern Time) and beginning April 20th, 2021 (Eastern Time) the Yahoo Answers website will be in read-only mode. There will be no changes to other Yahoo properties or services, or your Yahoo account. You can find more information about the Yahoo Answers shutdown and how to download your data on this help page.
Trending News
Where should I start troubleshooting this heat pump?
We have a Trane XE 900 heat pump. The air coming out is cool but not cold. It stopped working 2 days ago but we did get it to work last night by holding the fan in the outside unit still and turning it on with the thermostat inside. It ran all night just fine but this morning it quit again. We've cleaned the inside unit and put in new filters and also checked the drain hose for clogs. We took the cover and one side off the outside unit and blew it out with an air compressor hose so there is no grass or trash inside it. The inside unit is running normal, the outside unit fan is turning but still no cold air. Where do we go from here?
3 Answers
- JwalkerLv 49 years agoFavorite Answer
More info may be needed to answer your question. You mentioned holding the condenser fan before turning the stat on. Why? Was it not running and you had to give it a spin to get it going? When the fan was running did it sound normal? If you grab the motor shaft can you move it side to side? Moving the motor shaft up and down a little is ok but side to side is not. Not even a little. That is an indication that the motor is about to lock up.
If it was running fine and just quit and then it ran ok again and quit again, if I’ understand you correctly, then that eliminates many possible problems. From the info I have left it leads me to believe that it is either the cond. fan motor going out or a capacitor out. Most units use a dual capacitor for the fan and compressor but the Trane units sometimes have 2 or 3 capacitors wired in parallel. Look at the capacitors to see if they look swollen. You can take one off and set it on a flat surface. If it wobbles it’s swollen. It should set perfectly flat. That would be the cheapest fix.
If the capacitor(s) isn’t swollen that doesn’t mean it’s ok but it won’t cost much if you want to replace it.
So, we can eliminate several problems: low refrigerant, air flow or anything to do with the air handler or low voltage circuit, including the thermostat.
Check for play in the motor bearings by moving the shaft side to side.
Check the capacitor for burnt wires on the terminals or if it looks swollen.
You can email me if you like and we can get into greater detail.
- 6 years ago
fan on blower will not start unless you turn with your finger then it run fine until time to restart
- 9 years ago
before you damage anything more just call a HVAC tech to check it properly
Source(s): plumber for 27 years