Yahoo Answers is shutting down on May 4th, 2021 (Eastern Time) and beginning April 20th, 2021 (Eastern Time) the Yahoo Answers website will be in read-only mode. There will be no changes to other Yahoo properties or services, or your Yahoo account. You can find more information about the Yahoo Answers shutdown and how to download your data on this help page.
Trending News
Problem calculating the current with a 3 phase motor?
<sigh> i know its trivial but i'm no more used calculating it, but now i need to and i'm unsure how it works.
i know P=U*I
but i know there was a factor for 3 phase engines like SQR(3)
now i'm confused how to proper calculate the current for a motor.
The plate on it reads 1.7 kw / 5.9 kw as i assume this is the wattage in star/delta config.
how much current do i have to expect in Delta or Star configuration at a voltage of 400 Volts phase to phase 230 Volts phase to neutral. how much current do i have to expect for startup ?
and how do i get there (thats even more important to know)
can someone help me ?
2 Answers
- Steve WLv 51 decade agoFavorite Answer
For three-phase motors, the calculations are:
P = sqrt(3) * U * I * cosphi * efficiency, where
P is rated power in Watts
U is line-line rms voltage, in Volts
I is line current in Amps,
cosphi is the power factor (i.e. cos(phi)) at rated power, and
efficiency is at rated power.
This formula is the same for delta and star-connected machines.
Typical starting currents are approximately 6 times the rated full load current, but the nameplate should provide some indication, either as a multiplier, an sKVA (starting kVA), or as a "code letter" (for ANSI/NEMA rated machines).
The 1.7 / 5.9 kW is a bit difficult to know for certain what the machine produce. If there are also comparable rated voltages, this could be understandable, since the motor rating is most likely based on a rated winding current.
At 5.9 kW, on a 400 V system, with an assumed cos(phi) = 0.85, and efficiency = 0.9, the motor full load current would be 11.1 Amps. Starting current would be approximately 66 Amps.
- GailLv 45 years ago
volts times amps = watts. A 300 kW (300,000 watts) at 240 volts can use up to 300,000/240 (roughly 1000) amps. that is, to put out the rated power requires than much current (or a ramping up of voltage inside the system by a transformer). frequency is a measure of the rate of back and forth motion in the AC circuit. Components tend to be "sized" to work at a certain frequency. Mismatch of frequency requirements can cause faulty operation or even failure of the equipment. As a very simple example, a conversion of AC to DC may use a diode and capacitor system to filter and flatten the output signal. The components are designed for a certain rate of signal and will not do as designed (and could fry) if input frequency is not as expected.