Yahoo Answers is shutting down on May 4th, 2021 (Eastern Time) and beginning April 20th, 2021 (Eastern Time) the Yahoo Answers website will be in read-only mode. There will be no changes to other Yahoo properties or services, or your Yahoo account. You can find more information about the Yahoo Answers shutdown and how to download your data on this help page.

Electric clothes dryer circuit-50 amp?

The circuit breaker already installed is 50 amp with 8 ga. wire. New dryer is 30 amp. Can I just change the plug to 30 amp? Change the breaker to 30 amp and keep 8 ga. wire? or does it all have to change? Thanks

9 Answers

Relevance
  • 9 years ago
    Favorite Answer

    Change the breaker

    Change the receptacle

    Leave the wire

    #8 AWG romex feeding a receptacle should not be fed by a 50 amp breaker for any reason.

    If the UL nameplate on the dryer says 30 amp then it is only legal by NEC to use a 30 amp breaker. Worst case scenario: if the motor goes bad or the drum freezes up and puts a high load on the motor the motor could overhead and start a fire before the breaker trips if left on a 50 amp breaker.

    Use a 4 wire receptacle http://www.amazon.com/gp/product/B00009W3A9/ref=as... and cord if 4 wires are present, if 3 wires are present then normally it was installed while that was still allowed by code, and can remain a 3 wire installation http://www.amazon.com/gp/product/B00002NARC/ref=as... .

    Source(s): Local 46 Electrician National Electrical Code, which is written by the National Fire Protection Association
  • 9 years ago

    Yes you can change the receptacle and the breaker to 30 amp and keep the same wire. No problem at all.

    Those telling you to leave the 50 amp breaker are wrong.

    Source(s): Electrician
  • Tony
    Lv 7
    9 years ago

    You can leave the heavier wire. But going the other way (from 30 to 50 amp) you WOULD need to upgrade the wiring.

    If you DO change the plug be sure to change the breaker too. It's not electrically necessary but it will avoid confusion in the future should you sell the house.

    Ava g'day mate.

    ")

    Source(s): Just an old retired dog who knows a few tricks.
  • 9 years ago

    New dryers require a grounded 4 prong outlet. If it is easy to change the wire I'd recommend changing it otherwise a 3 prong pigtail would be required to connect to your existing 3 prong ungrounded outlet. That is if your dyer is indeed ungrounded. Otherwise skip the above comments.

    With 30amp breaker and a #8 wire you have to pigtail the #8 to a #10 so the wire matches the breaker size. This is legal and safe.

    I just came back to reiterate it is not legal nor safe to put a #8 wire to a 30amp breaker. I'm "shocked" nobody else mentioned that in their posts.

    The correct way is to pigtail the #8 to #10.

    Source(s): class II master electrician
  • How do you think about the answers? You can sign in to vote the answer.
  • 9 years ago

    There's nothing wrong with the 50 amp breaker. A socket circuit has a big breaker on it but there might only be a 10 watt radio plugged in taking less than 1 amp, that doesn't mean the breaker is dangerous, just that it can supply a big load if required.

    If you want to use a smaller breaker it should be bigger than the load, so use a 40 amp one.

  • 9 years ago

    You can always go with a smaller breaker for the wire size. But it is dangerous to go with a LARGER breaker for the wire size.

  • 9 years ago

    I'd recommend a 35-40 AMP breaker, because they can get a little off, and you'd be better safe than sorry.

    Or don't do anything, if your dryer draws more amps than it needs, it won't be saved by a tripping breaker.

    You don't need to change the wire though, it's rated for more, but it can easily handle less.

  • Jim W
    Lv 7
    9 years ago

    Leave the wire, change the receptacle and the breaker.

  • CJlove
    Lv 6
    9 years ago

    Leave it alone, the 50 amp is fine for a 30 amp dryer.