Yahoo Answers is shutting down on May 4th, 2021 (Eastern Time) and beginning April 20th, 2021 (Eastern Time) the Yahoo Answers website will be in read-only mode. There will be no changes to other Yahoo properties or services, or your Yahoo account. You can find more information about the Yahoo Answers shutdown and how to download your data on this help page.
Trending News
Electrical....?
If you have a short but a ground connected to a device. Electrical current will flow through the ground when there is something wrong with right path. Does this mean that whatever the ground is connected to have current running through it at all times or just temporarily
With the
3 Answers
- mark_pocLv 63 months ago
The equipment grounding conductor never should have current flowing through it unless there is a short to ground, like if a hot wire in a machine contacts the outer metal casing. Then current will flow just long enough to trip the breaker to shut off the circuit.
The exception to this would be a small trickle current flowing all the time when a light dimmer or other fancy device is wired in place of a light switch. This is not a desired thing, but many switch boxes don't have a neutral wire in them so the ground wire is inevitably used as a neutral. I believe the NEC now requires a neutral wire to be present in every electrical box.
- billrussell42Lv 73 months ago
to start, "short but a ground connected to a device" is meaningless. A short to ground, do you mean?
"something wrong with right path" is also meaningless.
and the rest is also meaningless also. try again, in good English.